Here's a good one to practice some psych chart navigation. The more adventurous TFS folks might want to give this one a shot too. Have fun:
An air conditioning unit handles 111,000 SCFM of 100% outdoor air at 80F, 70% r.h. A single coil performs cooling and dehumidification. The coil's apparatus dew point is 55F, and the condensate is noted to flow out of the unit at a rate of 5 gallons per minute. Under these conditions, the coil bypass factor is most nearly:
(A) 0.10
(B) 0.15
(C) 0.20
(D) 0.25
An air conditioning unit handles 111,000 SCFM of 100% outdoor air at 80F, 70% r.h. A single coil performs cooling and dehumidification. The coil's apparatus dew point is 55F, and the condensate is noted to flow out of the unit at a rate of 5 gallons per minute. Under these conditions, the coil bypass factor is most nearly: