Help with solving short-circuit current

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Sparky Bill PE

Senior, Master, Professional, Licensed Electrical
Joined
Jun 30, 2019
Messages
303
Reaction score
149
Location
Chattanooga TN
To solve for short circuit current, do you just know you're supposed to take the phase voltage instead of the line voltage? Since the system was in 3-phase I wouldn't have thought to change. 

image.png

image.png

 
Yes.  Since impedence is always a "per phase" quantity, you need to use phase voltage when solving for the current.  If you were given that this was a delta source, you could assume the line voltage=phase voltage, but the problem doesn't state this, so you must assume line voltage and convert to phase. 

 
What DuranDuran said.

Basically, short-circuit current or fault current is a line current quantity. So typically you use the line-to-neutral voltage phasor and divide that by the total impedance between the source and the fault location to obtain the fault current (line-current) phasor value.

 
Back
Top