Help needed for NCEES #530

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

AD_power

Member
Joined
Aug 29, 2012
Messages
5
Reaction score
0
If somebody knows from what magic hat they pulled additional impedance of 0.025??? Transformer connected to the bus, it should be pretty simple and straightforward solution:

Isc= I on 480v side (1203A) / Z of transformer (0.04). I'm confused.

 
Your solution is only valid if for the "infinite bus" on the utility side. In this case they give you the capability of that side.

 
When using the per-unit method there is an impedance associated with the fault duty. This obtained first by getting the per-unit apparent power which is found by using the 1000kVA rating of the transformer the system's base apparent power and converting it into MVA, which is 1MVA. Next the fault duty's per-unit value is S=40MVA / 1MVA = 40p.u. . Next the per-unit impedancnce associated with the fault duty is z = 12 / 40 = .025pu. Next we find the per-unit fault current is

if = 1 / (.04+.025) = 15.38pu.Next the base current on the secondary side of the transformer where the fault occurs is Ib = (1000*103) / (sqrt(3) * 480 ) = 1202.81Amps

Finally we determine the acctual fault current by multiplying the per-unit fault current by the base current on the secondary side of the transformer.

IF = if * Ib = (15.38)*(1202.81) = 18499 Amps.

 
Back
Top