Something seems to be tripping me up on this problem.
I've tried to solve using the MVA method but I'm missing something.
Ex. 51:
Two generators are connected through two transformers to a bus that is connected to a transmission line. The line is open at the far end, where there is a three phase fault. Prior to the fault, the voltage at the end of the transmission line is 230KV. The ratings are per unit reactances of the equipment based on the equipment ratings are shown below:
G1 = 700 MVA, 12KV, X''d=X2=.11, X0=.06
G2 = 600 MVA, 12 KV, X''d=X2=.14, X0=.08
T1 = 700MVA, 12/230KV, delta/wye, X=.14
T2 = 600MVA, 12/230KV, wye/delta, X=.12
Transmission line = base of 1000MVA, 230KV, X1=X2=.19, X0=.45
All wye winding neutrals are solidly grounded.
Find fault current.
I've tried to solve using the MVA method but I'm missing something.
Ex. 51:
Two generators are connected through two transformers to a bus that is connected to a transmission line. The line is open at the far end, where there is a three phase fault. Prior to the fault, the voltage at the end of the transmission line is 230KV. The ratings are per unit reactances of the equipment based on the equipment ratings are shown below:
G1 = 700 MVA, 12KV, X''d=X2=.11, X0=.06
G2 = 600 MVA, 12 KV, X''d=X2=.14, X0=.08
T1 = 700MVA, 12/230KV, delta/wye, X=.14
T2 = 600MVA, 12/230KV, wye/delta, X=.12
Transmission line = base of 1000MVA, 230KV, X1=X2=.19, X0=.45
All wye winding neutrals are solidly grounded.
Find fault current.