It depends on which phase to phase fault occurred. IA=0 if there is Phase B to Phase C fault.So this is a phase to phase fault question. I thought that IA = 0 in phase to phase faults?
View attachment 12636
Yes, will do.Justin,
Cheat sheet looks good. hope you can have a final version in a few weeks before the april 2019 exam. Can you please update it here when the final version is out?
I will send an email out to those that purchased a engproguides product. I am looking at a couple of weeks from today.@justin-hawaii
For those that purchased the Engproguides, will an e-mail be sent out to download the updated version and if so, how long until release?
Sorry about the confusion with the two different formulas. You will get the same magnitude with both formulas, it is just the angle of currents will be 90 and -90 vs. 30 and -30. Since the angles are relative, both will satisfy the solution. The derivation of the a^2 - a term can be seen below.I'm sure I'm just missing something simple here. This a part of the solution where the sequence current is converted into phase current.
View attachment 12664
That equation does not match the equation used in the EPG study guide. The study guide has 𝐼𝐵 = 𝐼𝐴1 ∗ (𝑎^2 − 𝑎) and i understand that IA=-IB. Can anyone explain this part of the solution (just how this formula was determined)?