The wording of the solution is pretty convoluted and hard to follow, but here is my take on it judging by the diagram and the math:
I_s = Power transformer secondary current
I_2 = Delta connected CT phase current on the secondary side of the power transformer
I_2,relay = Delta connected CT line current leaving the delta connection, entering the relay, on the secondary side of the power transformer
I_2,relay would be equal to √3·I_2, and not equal to I_2/√3 since it is the line current exiting the delta connected CTs:
I_2,relay = √3·I_2
There would also be a lagging (negative) 30 phase shift in the phase angle of the I_2,relay current compared to I_2 assuming balanced and positive sequence conditions.
Another interesting observation is the solution setting I_1,relay equal to I_2,relay. This would only be true for a 1:1 ratio power transformer with equal primary and secondary CT ratios.
Just my 2 cents.