A AAGR2013 Active member Joined Jul 29, 2015 Messages 31 Reaction score 4 Oct 10, 2016 #1 the table in NEC2014 is always referenced to find out the conductor capacity. I am still not sure the difference by reading the title of table. Last edited by a moderator: Oct 10, 2016
the table in NEC2014 is always referenced to find out the conductor capacity. I am still not sure the difference by reading the title of table.
knight1fox3 Jedi MASTER & Friend of Capt. Solo Joined Dec 30, 2009 Messages 16,366 Reaction score 4,067 Location Brew City! Oct 10, 2016 #2 The first table is for current-carrying conductors in raceway, cable, or earth. The second table is for current-carrying cables in free air (e.g. connecting power dist./control panels together).
The first table is for current-carrying conductors in raceway, cable, or earth. The second table is for current-carrying cables in free air (e.g. connecting power dist./control panels together).
A AAGR2013 Active member Joined Jul 29, 2015 Messages 31 Reaction score 4 Oct 10, 2016 #3 thanks, free air seems to be wire/cable is not in tray, conduit... I assume it runs in short distance because there is no support.
thanks, free air seems to be wire/cable is not in tray, conduit... I assume it runs in short distance because there is no support.
TWJ PE Well-known member Joined May 1, 2014 Messages 1,543 Reaction score 190 Location Texas Oct 11, 2016 #4 AAGR2013 said: thanks, free air seems to be wire/cable is not in tray, conduit... I assume it runs in short distance because there is no support. Click to expand... Don't think of it that way....
AAGR2013 said: thanks, free air seems to be wire/cable is not in tray, conduit... I assume it runs in short distance because there is no support. Click to expand... Don't think of it that way....