Here are the details of what I've been thinking about...
Primary side data:
-delta connection
-13.8kV
-impedance assumed negligible
Secondary side data:
-wye ground connection
-4160V
-impedance assumed negligible
Xmer data:
-let's say for argument's sake 5MVA
Load data:
-let's say a total of 3000hp load connected to secondary side....single bus system. from 1 switchgear to 1 mcc
-assume 0.9 PF
-assume 1.0 diversity factor
-------------
thought process...of trying to find current on primary side.
P=3000hp*746*1.0=2237kW (real power)
S=2237kW/0.9=2486kVA (apparent power)
Q= sqrt(2486^2 - 2237^2)= 1084kVAR(reactive power)
I (secondary)=2486kVA/4160V/sqrt3=345A (current on secondary)
transformation from wye secondary to delta primary:
use turns ratio...we know:
Vp/Vs=Is/Ip
13800V/4160V=345A/Ip(delta)
Answer: Ip(delta)=104A
Does that look OK to you?
Thank you.
Primary side data:
-delta connection
-13.8kV
-impedance assumed negligible
Secondary side data:
-wye ground connection
-4160V
-impedance assumed negligible
Xmer data:
-let's say for argument's sake 5MVA
Load data:
-let's say a total of 3000hp load connected to secondary side....single bus system. from 1 switchgear to 1 mcc
-assume 0.9 PF
-assume 1.0 diversity factor
-------------
thought process...of trying to find current on primary side.
P=3000hp*746*1.0=2237kW (real power)
S=2237kW/0.9=2486kVA (apparent power)
Q= sqrt(2486^2 - 2237^2)= 1084kVAR(reactive power)
I (secondary)=2486kVA/4160V/sqrt3=345A (current on secondary)
transformation from wye secondary to delta primary:
use turns ratio...we know:
Vp/Vs=Is/Ip
13800V/4160V=345A/Ip(delta)
Answer: Ip(delta)=104A
Does that look OK to you?
Thank you.