I'm a little confused at one particular question (question 50) from Cram for PE Power Exam volume 2, about 3-phase capacitor bank. The question is:
"A 3-phase wye-connected capacitor bank is installed at a 69-KV substation. The capacitor bank consists of 3 single-phase capacitor banks. Each bank consists of 4 parallel and 7 series capacitor units. Each capacitor unit is 5 KV and 100 KVAR. What is the nominal power rating in KVAR for the 3-phase capacitor bank?"
My understanding is that the KVARs of each capacitor unit simply get added up, regardless of whether the capacitors are in series or in parallel. So my initial take was:
Q 1-ph = (4 + 7) x 100 KVAR = 1100 KVAR
Q 3-ph = 3 x Q 1-ph = 3 x 1100 KVAR = 3300 KVAR
However, the solution states:
Q = 3 x 4 x 7 x 100 KVAR = 8400 KVAR
Why multiply the 4 and 7, if the problem states that each bank has 4 parallel and 7 series capacitor units? Am I missing something or not understanding something correctly?
I'm a little confused at one particular question (question 50) from Cram for PE Power Exam volume 2, about 3-phase capacitor bank. The question is:
"A 3-phase wye-connected capacitor bank is installed at a 69-KV substation. The capacitor bank consists of 3 single-phase capacitor banks. Each bank consists of 4 parallel and 7 series capacitor units. Each capacitor unit is 5 KV and 100 KVAR. What is the nominal power rating in KVAR for the 3-phase capacitor bank?"
My understanding is that the KVARs of each capacitor unit simply get added up, regardless of whether the capacitors are in series or in parallel. So my initial take was:
Q 1-ph = (4 + 7) x 100 KVAR = 1100 KVAR
Q 3-ph = 3 x Q 1-ph = 3 x 1100 KVAR = 3300 KVAR
However, the solution states:
Q = 3 x 4 x 7 x 100 KVAR = 8400 KVAR
Why multiply the 4 and 7, if the problem states that each bank has 4 parallel and 7 series capacitor units? Am I missing something or not understanding something correctly?