In this problem the full load amps of the 150hp, 460V, 3 phase motor is 180A per NEC. But in the book they didn't multiply the 180x1.25 as required by NEC 430.22 to size branch circuit conductors so they selected the 4/0 AWG instead of the 300KCM that will require with the 1.25 multiplier. Any ideas?