I have a question regarding a given solution. Given the following parameters, can you show me the work to find the transformer's efficiency?
Given Tx:
20kVA
6.6/2.8 kV
Core Loss = 75 W
Copper Loss = 241 W
Is = 6.6<-22 A , where Is = secondary current
The formula I would use is:
Eff = Pout/(Pout + P losses)
Eff = (2.8 kV)(6.6 A)(cos(-22)/[((2.8 kV)(6.6 A)(cos(-22))+75+241] , where I get Pout = 18.479.28 kW
Eff = 98.3%
The closest answer is 98.2% (which is also marked as the correct answer), but the solution shows that Pout = 17.1 kW.
Has anyone else come across this difference?