Should the answer for this problem be letter C?
First thing is, 180A is not a standard size breaker. Second is, per NEC Art.240.4(B)(2), if the ampacity of the conductor does not correspond with the standard ampere rating of a fuse or breaker, we can use the next higher standard size.
Does anyone agree?