Problem:
"Of the rated current listed below, which is the largest allowable for an overcurrent device to protect a 300kcmil, TW, 60degree Aluminum conductor feeding a 277V load. Assume conductor is in a steel conduit.
A. 150 A
B. 180 A
C. 200 A
D. 225 A
"
NEC says 300kcmil, TW at 60 degrees Aluminum, it is rated for 195 A. NEC 240 says, next highest standard device rating. I got 200A, C. The book says the conductor is rated for 190 A and chose B. Is this an error on them?