I hope someone can help me with the followings.
1) On volume 1 question 5, I have I=1500/(2.4+j3.4)=360.43 at angle -54.78 or 207.85-j294.46. But the answer shows 358A. Please advise.
2) On volume 1 question 13, what is SCA? Could you explain to me how it works? My understanding is that the transformer secondary side can only supply the max current 130A.
3) On volume 1 question 30, when we calculate the real power, how come we don't include the power factor 0.78 lagging?
4) On volume 1 question 69, I think the answer should be c. 200A. According to NEC 2014 240.4 (B), the next higher standard overcurrent device rating (NEC 240.6) shall be permitted. 180A is not even the standard size per NEC 240.6.
Thanks!