Hi guys,
I have a question regarding sizing a conductor for a 150 HP motor, based from the Complex Imaginary PE Power Set 4 exam.
This is question 67 from Set 4 of the Complex Imaginary PE Power Set 4 exam:
"What is the minimum required size for the single-insulated, 60-degree C, TW, copper conductors feeding a 460 V, 3-phase, AC motor rated 150 HP operating on continuous duty?"
The thing that confuses me is what I don't see in the provided solution.
The given solution says to refer to NEC Table 430.250 to find the full load current of a 3-phase, 460 C, 150 HP motor, which is 180 A.
However, it does not then multiply this FLC by 125%, which I would expect for a continuous duty motor. The provided solution simply uses this 180-A full-load current to size the conductors.
Is there some sort of exception that I'm not seeing in the NEC regarding higher-HP motors not needing the 125% multiplier for continuous duty? I thought that all continuous-duty motors need the 125% multiplier to their full-load current, and I never saw any exceptions regarding higher HP on motors. Is it possible that this given solution is incorrect?
I appreciate anyone who spends their time helping me on this!
I have a question regarding sizing a conductor for a 150 HP motor, based from the Complex Imaginary PE Power Set 4 exam.
This is question 67 from Set 4 of the Complex Imaginary PE Power Set 4 exam:
"What is the minimum required size for the single-insulated, 60-degree C, TW, copper conductors feeding a 460 V, 3-phase, AC motor rated 150 HP operating on continuous duty?"
The thing that confuses me is what I don't see in the provided solution.
The given solution says to refer to NEC Table 430.250 to find the full load current of a 3-phase, 460 C, 150 HP motor, which is 180 A.
However, it does not then multiply this FLC by 125%, which I would expect for a continuous duty motor. The provided solution simply uses this 180-A full-load current to size the conductors.
Is there some sort of exception that I'm not seeing in the NEC regarding higher-HP motors not needing the 125% multiplier for continuous duty? I thought that all continuous-duty motors need the 125% multiplier to their full-load current, and I never saw any exceptions regarding higher HP on motors. Is it possible that this given solution is incorrect?
I appreciate anyone who spends their time helping me on this!