problem: Calculate the minimum size of TW type copper conductors required to feed a 45KVA 3 phase continuous load from a 480V/277V 3 phase 4 wire power distribution board. The temperature rating of equipment terminals is 60 C( 140F)
The solution uses 45K/(sqrt 3*480) to calculate the ampacity. My question is that should we use
45K/(sqrt 3*277) ? I assume that the load is connected to the 277 side.
The solution uses 45K/(sqrt 3*480) to calculate the ampacity. My question is that should we use
45K/(sqrt 3*277) ? I assume that the load is connected to the 277 side.