iahim
Well-known member
- Joined
- Nov 16, 2012
- Messages
- 132
- Reaction score
- 3
What is the internal generated phase voltage for a 3-phase synchronous generator with per unit reactance of 1.1 and steady-state current of 0.97 pu. Base values: 250kV, 100MVA.
The CI solution is V=iX=1.07pu, or 268V. Is that correct?
I think the internal generated phase voltage should be the terminal voltage (L-N) plus iX = 1+1.07 = 2.07 pu. Vbase LN = 144V, so the solution should be 298V.
Thanks!
The CI solution is V=iX=1.07pu, or 268V. Is that correct?
I think the internal generated phase voltage should be the terminal voltage (L-N) plus iX = 1+1.07 = 2.07 pu. Vbase LN = 144V, so the solution should be 298V.
Thanks!