The power consumed by any load( for the time being let us forget VARs generated or consumed) is I**2*X or V**2/X(replace I=V/X). So this gives us X=P/I**2 or V**2/P. Coming to three phase system where three phase power is given. P(3phase)=3*Vp**2/Xp . Now let me replace Vp=Vl/sqrt3 in this; it gives me P=Vl**2/Xp. I am not solving them for Xp because that is very easy from here.Hi all,
just a quick one,
for a 3 phase system, we have V line and total reactive power consumed by the system Q.
then capacitive reactance Xc = V line**2/Q or sqrt(3)*V line**2/Q ? This is totally wrong.
I am confused.
But you always have a different way of explaining the concept. To be honest I get it by reading it two times but it is interesting to understand the same thing in different way. I always believed EE is more of maths but some of you guys present it in a artistic way. I appreciate that. I for that matter will simply take it to maths after the concept and understand from there. I am really skeptical about how many follows my maths here.
Thanks rg1,The power consumed by any load( for the time being let us forget VARs generated or consumed) is I**2*X or V**2/X(replace I=V/X). So this gives us X=P/I**2 or V**2/P. Coming to three phase system where three phase power is given. P(3phase)=3*Vp**2/Xp . Now let me replace Vp=Vl/sqrt3 in this; it gives me P=Vl**2/Xp. I am not solving them for Xp because that is very easy from here.
Now coming to your specific question if you are taking power as 3 phase take Line Voltage. If you are taking 1/3 of given 3 phase power take Phase voltage. But formula remains same X= V**2/Q(P) and do not mix the two, it will create havoc.
If it does not make sense I will try to phrase it in a different way .
Yes Xc is phase value. To make it simple to understand I started from single phase. You can read my first post again. P(3phase)=3*Vp**2/Xp. Whenever there is a confusion in understanding, imagine star grounded system. Three separate single phases. Start from there and come over to 3 phase, you will get a sense what is what? There are many ways to do a thing, if they have used sqrt3, I in absence of what exactly they have done, I can not comment, may be right. I have seen these guys sometimes using some weird thing to get an answer. If they want 15 they will simply multiply 3 with 5 and then introduce EE into that, to explain you. Lol. Post the details, we will discuss it further.Thanks rg1,
this is what I thought, but I faced one problem where they used the sqrt(3) formula. I will post later.
Anyway, Xc we get, is it total or per phase?
here we goYes Xc is phase value. To make it simple to understand I started from single phase. You can read my first post again. P(3phase)=3*Vp**2/Xp. Whenever there is a confusion in understanding, imagine star grounded system. Three separate single phases. Start from there and come over to 3 phase, you will get a sense what is what? There are many ways to do a thing, if they have used sqrt3, I in absence of what exactly they have done, I can not comment, may be right. I have seen these guys sometimes using some weird thing to get an answer. If they want 15 they will simply multiply 3 with 5 and then introduce EE into that, to explain you. Lol. Post the details, we will discuss it further.
I took a ton of classes in this area and enjoyed it even though my GPA suffered for it. I don't use any of it directly because I ended up as a Power Engineer, although it does help me to know what Protective Relays are actually doing.The "math" you speak of in EE is in the DSP and communications fields. Damn, what a nightmare. I enjoyed Fourier and Laplace analysis. The magic of these operations are purely genius, especially, after you're able to wrap your mind around what these operations are actually doing and how a time domain signal is decomposed into complex sines/cosines to show a complete spectral representation. That said, I'm much happier on this side of the fence. I could never do another Fourier transform and be as happy as a pig in mud. Same for Laplace, convolution integrals, etc.....
So as I said, to understand better, assume it to be star connected load. 150VA is 3 phase reactive power to be compensated. So single phase power is 150/3=50VA and single phase Voltage is 208/sqrt3. Now it becomes simple.
Omer it will be good idea if you post your both maths (assuming load to be star as well as delta) on the forum for benefit of many.So as I said, to understand better, assume it to be star connected load. 150VA is 3 phase reactive power to be compensated. So single phase power is 150/3=50VA and single phase Voltage is 208/sqrt3. Now it becomes simple.
Even if you assume it to be a delta connection, answer will be same, your maths will be longer and understanding may be better after you do that. I will suggest you to do it bothways to understand the stuff. Even in delta one phase power will be 50VA, because each phase has to share it equally.
Q=V^2/X=wCV^2
if we assumed delta connection, as you suggest power per phase is 50VA, however voltage across the capacitor is 208 V line voltage compared to 208/sqrt(3) across capacitors in wye connection. therefore, answer will be different. Is it so?So as I said, to understand better, assume it to be star connected load. 150VA is 3 phase reactive power to be compensated. So single phase power is 150/3=50VA and single phase Voltage is 208/sqrt3. Now it becomes simple.
Even if you assume it to be a delta connection, answer will be same, your maths will be longer and understanding may be better after you do that. I will suggest you to do it bothways to understand the stuff. Even in delta one phase power will be 50VA, because each phase has to share it equally.
You are absolutely right. This will help us in better understanding , what is happening there. If you get Xy in Star connection you get 3*Xy in Delta connection. Right?. If you convert this Xd again into Xy by conversion methods of delta to star of impedance you again get the same answer as you got with star calculations directly. That proves we are correct. So far we are on correct path. Is it? We will come to specific question next.if we assumed delta connection, as you suggest power per phase is 50VA, however voltage across the capacitor is 208 V line voltage compared to 208/sqrt(3) across capacitors in wye connection. therefore, answer will be different. Is it so?
Ok, that mean capacitance required is different depending on the connection.You are absolutely right. This will help us in better understanding , what is happening there. If you get Xy in Star connection you get 3*Xy in Delta connection. Right?. If you convert this Xd again into Xy by conversion methods of delta to star of impedance you again get the same answer as you got with star calculations directly. That proves we are correct. So far we are on correct path. Is it? We will come to specific question next.
The question asks total capacitance. They seem to be attempting for that. I have check it. But that is not the way. There is nothing like total capacitance. The capacitance in star connection will have less Voltage rating and more current rating( less Xc more C); capacitance in delta will have more voltage rating and less current rating (more Xc less C). And we say 3 capacitors of this particular ratings are required. Generally we measure total capacity in VARs and not in Farads. Because total of anything (R,L,C) will depend on how you connect them(series parallel combination). Your confusion is justified.Ok, that mean capacitance required is different depending on the connection.
will assume for this specific question star as it is usually the case. This is what I have seen in some text books including Wildi which says if nothing is mentioned do it with star. this will result in capacitance of 9 micro farad per phase. By doing in it both ways and getting the same (lol) answer we at least are sure that we are right. I do not think we have done anything wrong.
what confused me from the beginning was the solution provided. I think they are mistaken somehow.
View attachment 9894
IMHO. Base Z= BaseV/BaseI. In which both V and I are the Voltage across and current through a load. There is no Z as three phase. You start from Vp and Ip for any thing star or delta. The formula given by you should be derived from here.A scenario to consider:
Why do you use Vline^2/Sbase when calculating base impedance in per unit, 3-phase analysis? Why not phase voltage, if practical and other necessary conversions are performed?
Enter your email address to join: