@SparkyBill Sorry I didn't elaborate earlier, I was headed out of the house.
The restrictions go with the formulas. but they will also work for 3 phase too. I don't know why they've restricted it to 1 phase transformers. Granted your problem up there doesn't specify what kind of transformer.
With the handbook formulas, you can also make the ones like this:
SL1 = SL2* ((ZT2%)*ST1) / (ZT1%)*ST2)
SL2 = SL1* ((ZT1%)*ST2) / (ZT2%)*ST1)
First solve for SL1 using SL2 = ST2... because you know you'll be maxing out 1 transformer, but you need to figure out which one you'll be maxing out.
Then solve for SL2 using SL1 = ST1.
one of your answers for SL1 or SL2 from your math above is going to be larger than the ST1 or ST2 value. That transformer will be overloaded in that situation, therefore it is the limiting transformer.
After that you know you'll be fully loaded on your limiting transformer, and then loading your other transformer to the SL1 or SL2 value you calculated above for the other transformer.
--------
For the problem you've given above, I'd solve like this
SL1 = 8MVA * ((2%*6MVA) / (3%*8MVA)) = 4MVA
SL2 = 6MVA * ((3%*8MVA) / (2%*6MVA)) = 12MVA
12MVA is larger than the 8 MVA transformer, therefore the 8MVA transformer is your limiting transformer because it can only load up to 8MVA.
-------
Zach's Power Flow section has a lot of the derivations if you want to review that, I find his notation to be a tad confusing though.
Another white paper that you might find helpful is this one from schneider electric:
https://www.se.com/us/en/download/document/7400DB0701/