I have a question regarding the books answer to this problem. It states that for this case, circuits less than 100A you need to use the 60degC column for cable ampacities. Is this because they only give the terminal ratings of the OCPD and not the field devices? The code will allow the use of 75degC as long as the equipment, etc is rated appropriately.
Thanks!