I'm working some problems and am confused about 2 very similar problems, and can't quite figure out why. My issue is that the solution methods are identical, yet in one they use a mysteriously appearing square root of 3, and the other has no square root of 3. Which one is right, and/or why is that root 3 in there?
Here we go.
Problem 1:
You're given a 3 phase induction motor that is running at 480 volts and it's reactive component is 57,790 vars. What is the PER PHASE capacitance (farads) needed to correct the power factor to 1.0? (if you need it, current total power output is 109,705 VA at a .85 power factor)
Problem 2:
You want to correct a 1406 kVA .99 power factor load. I calculated ~180 kVAR oughta do it. Voltage is 6900 Y. What is the PER PHASE capacitance (farads) to correct it to 1.0?
Answers:
#1, I got 128x10^-6, their solution worked out like this:
Q=57.8 kVARS, PF=1.0
Qphase=Q/3=19.26 kVARs
Cphase=Qphase=Qc: :wv: ::^2)=[19260]/[377*(480)^2/sqrt(3)]=222x10^-6 Farads
Where did that sqrt 3 come from? I worked it a different way. I did:
1/(2*pi*f*C)=V^2 * sqrt(3)/Q and solved for C, then divided by 3. Maybe I needed to divide by square root of 3 instead of 3, because we're going line to neutral with the caps. I can understand that.
But, #2 solution has no square root of 3.
#2, I got 9.8x10^-6, their solution:
Q=180 KVARs
Qphase=Q/3=60 kVARs
Cphase=Qphase=Qc/: :wv: ::^2)=[60000]/[377*(6900)^2]=3.34x10^-6
What I did was to divide Q/3 first to get 60, and then used my formula above, and instead of line to line voltages, I used line to neutrals in my formula. If you divide my answer by 3, you get their answer (which could be associated with my line to phase conversion).
Since neither of my answers matched, and they are using different formulas to solve pretty much the same exact problem, I don't know who is right. lol.
Thanks for reading. Any insight is appreciated.
Or if anyone has a quick and known good formula for this I can just scribble down in my book, that'd work for me too, lol.
Edit: and what's with my omega-V's becoming the West Virginia symbol? Bwah ha.
Here we go.
Problem 1:
You're given a 3 phase induction motor that is running at 480 volts and it's reactive component is 57,790 vars. What is the PER PHASE capacitance (farads) needed to correct the power factor to 1.0? (if you need it, current total power output is 109,705 VA at a .85 power factor)
Problem 2:
You want to correct a 1406 kVA .99 power factor load. I calculated ~180 kVAR oughta do it. Voltage is 6900 Y. What is the PER PHASE capacitance (farads) to correct it to 1.0?
Answers:
#1, I got 128x10^-6, their solution worked out like this:
Q=57.8 kVARS, PF=1.0
Qphase=Q/3=19.26 kVARs
Cphase=Qphase=Qc: :wv: ::^2)=[19260]/[377*(480)^2/sqrt(3)]=222x10^-6 Farads
Where did that sqrt 3 come from? I worked it a different way. I did:
1/(2*pi*f*C)=V^2 * sqrt(3)/Q and solved for C, then divided by 3. Maybe I needed to divide by square root of 3 instead of 3, because we're going line to neutral with the caps. I can understand that.
But, #2 solution has no square root of 3.
#2, I got 9.8x10^-6, their solution:
Q=180 KVARs
Qphase=Q/3=60 kVARs
Cphase=Qphase=Qc/: :wv: ::^2)=[60000]/[377*(6900)^2]=3.34x10^-6
What I did was to divide Q/3 first to get 60, and then used my formula above, and instead of line to line voltages, I used line to neutrals in my formula. If you divide my answer by 3, you get their answer (which could be associated with my line to phase conversion).
Since neither of my answers matched, and they are using different formulas to solve pretty much the same exact problem, I don't know who is right. lol.
Thanks for reading. Any insight is appreciated.
Or if anyone has a quick and known good formula for this I can just scribble down in my book, that'd work for me too, lol.
Edit: and what's with my omega-V's becoming the West Virginia symbol? Bwah ha.