Good afternoon Lim,
Is there any way you could help me out with problem 80 from the NCEES practice exam? It pertains to acoustical control throughout a ductwork.
Thank you.
I had the same problem. Seems like we need some data on the noise control liner material. And I looked up on the Internet, different material really has very different properties. Also, there isn't any reference data on Ncees reference manual. So I came up with this solution, If we really come cross this question during exam.
Just remember at 1000 hz it has the highest noise reduction, about 2.3 dB/ft
So for this specific problem, at 1000 hz, it goes down to 96-23=73. And towards 2 directions of frequency the per foot reductions are all less than 2.3. Option C matches the pattern.
Just memorize 2 numbers. 2.3 dB/ft and 1000 hz. Without reference, I think this is the best we can do.
Since we are talking about noise control, there is another formula I memorized.
Experienced sound level.
Say there is a printer in an office, giving out 100 dB noise, frequency is 1000 hz . You sit 25 feet from it. Room volume is 250 cft. What noise level down you experience?
I don't think I could find the formula on the reference manual. But any way, this is the formula.
Lp=Lw-5logV-3logF-10logR+25
Lp: experienced level
Lw: sound source level 100 dB
V: room volume 250 cft
F: frequency 1000 hz
R: distance from sound source 25 ft
So the answer should be 90 dB.
Hope I'm helping. My exam is on the 22nd this month. What about you?