Hey guys,
I have a question about transformer short circuit tests specifically for 3-phase transformers. This comes from Cram for Exam Vol. 2 question 58.
In this problem, there is a 3-phase transformer given rated as 30 MVA, 130 KV/22 KV, wye-delta. The given short circuit test results are:
Short Circuit Test: 13 KV, 130 A, 110 KW
The 13 KV given in the short-circuit test is not specified as L-L or L-N, but I assume this to be L-L.
The question asks what is the total leakage impedance. In the given solution:
V SC = 13000 V / √3 = 7514 V
Leakage impedance Z = V SC / I SC = 7514 V / 130 A = 57.8 ohms
The solution also states that "the short circuit test uses the high voltage side of the transformer which is wye connected. Therefore, the per-phase voltage is given by V SC" (see above).
My question is: Is V SC the phase voltage measured from the winding during the short-circuit test? Or is it the line-to-neutral voltage during the SC test?
Put another way: if the HV side was delta instead, would V SC = 13000 V?
Thanks for any clarification on this!
I have a question about transformer short circuit tests specifically for 3-phase transformers. This comes from Cram for Exam Vol. 2 question 58.
In this problem, there is a 3-phase transformer given rated as 30 MVA, 130 KV/22 KV, wye-delta. The given short circuit test results are:
Short Circuit Test: 13 KV, 130 A, 110 KW
The 13 KV given in the short-circuit test is not specified as L-L or L-N, but I assume this to be L-L.
The question asks what is the total leakage impedance. In the given solution:
V SC = 13000 V / √3 = 7514 V
Leakage impedance Z = V SC / I SC = 7514 V / 130 A = 57.8 ohms
The solution also states that "the short circuit test uses the high voltage side of the transformer which is wye connected. Therefore, the per-phase voltage is given by V SC" (see above).
My question is: Is V SC the phase voltage measured from the winding during the short-circuit test? Or is it the line-to-neutral voltage during the SC test?
Put another way: if the HV side was delta instead, would V SC = 13000 V?
Thanks for any clarification on this!