    NEC reference cards ok to bring?

    Read through this:  pencil and paper section.  Don't lose out to a technicality.
  2. cos90

    Induction Machine

    Where did you get this Kaplan? Kaplan changed their name to Brightwood and the book I purchased from them looks nothing like this.
  3. cos90

    differential protection on 3 phas TXR

    You could also see a wye-delta used as a grounding bank, used like a zigzag transformer.
  4. cos90

    differential protection on 3 phas TXR

    A GSU is a delta-wye. I misspoke. The LV winding is the primary on a GSU transformer.
  5. cos90

    differential protection on 3 phas TXR

    My apologies for starting this discussion. Here's how you would solve this problem before microprocessor relays came onto the scene: @TNPE  you would see a wye-delta transformer applied for Generator Step Up (GSU), the tertiary of a large autotransformer, and at interconnection sites where...
  6. cos90

    differential protection on 3 phas TXR

    Here is the text: In our example, the transformer has the Δ-Y connection. Traditionally, CTs on the Wye connected transformer winding (winding 2) are connected in a delta arrangement, which compensates for the phase angle lag introduced in the Delta connected winding (winding 1), so that line...
  7. cos90

    differential protection on 3 phas TXR

    what if you lose feed from the utility and they close back in before you have someone at the station to turn the differential off? lockout differential on inrush ? genuinely curious 
  8. cos90

    differential protection on 3 phas TXR

    page 372  5.5.4.6 Phase and zero sequence compensation 
  9. cos90

    PPI

    Just beware it's not perfect and inspired my forum username  cos(180) = 0 ??????
  10. cos90

    PPI

    It's in the code: the nameplate rating is used for overloads only. Everything else is in those motor tables. Also the PPI exams were really tough.
  11. cos90

    differential protection on 3 phas TXR

    oh i forgot to mention a major source of CT error as mentioned by rg1: variation from the load tap changer!!  also if you are not tnpe or rg1 this discussion is way out of scope for the pe exam
  12. cos90

    differential protection on 3 phas TXR

    @rg1 you have done a good job explaining the details of transformer differential protection @TNPE I am curious what your plan is for the second energization of your transformers if you don't enable differential protection during the first energization?? especially since the next time you...
  13. cos90

    Capacitor Banks - calculating series/parallel kVAR

    thank you for finding these.
  14. cos90

    Capacitor Banks - calculating series/parallel kVAR

    Its a really straightforward question: You need to connect 3000kVAR to correct the power factor and you have 100kVAR cans How many cans per phase do you need to connect? 3000/3 = 1000 kVar per phase  1000kVAR/100kVAR = 10 cans per phase Where the questions get strange he draws out networks...
  15. cos90

    Any FE waiver case?

    I am glad to see you got it. I was worried for you when I saw this question. I was afraid to do anything out of the ordinary for my application.