NEC 310.15 - Ampacity
Also here is this:
310.4 Conductors in Parallel
By Mike Holt
Ungrounded and grounded neutral conductors sized 1/0 AWG and larger can be connected in parallel (i.e., electrically joined at both ends).
When conductors are run in parallel, the current must be evenly distributed between the individual parallel conductors. This is accomplished by ensuring that all ungrounded and grounded neutral conductors within a parallel set are identical. Each conductor of a parallel set must:
Be the same length.
Be made of the same conductor material (copper/aluminum).
Be the same size in circular mil area (minimum 1/0 AWG).
Use the same insulation material (like THHN).
Terminate in the same method (set screw versus compression).
In addition, raceways or cables containing parallel conductors must have the same physical characteristics and the same number of conductors in each raceway or cable. Conductors for one phase (ungrounded conductor) or the grounded neutral conductor, aren't required to have the same physical characteristics as those of another phase or grounded neutral conductor to achieve balance.
The equipment grounding (bonding) conductors for circuits in parallel must be identical to each other in length, material, size, insulation, and termination. In addition, each raceway (where required) must have an equipment grounding (bonding) conductor sized in accordance with 250.122. The minimum 1/0 AWG rule of 310.4 doesn't apply to equipment grounding (bonding) conductors [250.122(F)(1)].
When more than three current-carrying conductors are run together in a raceway longer than 24 inches, the ampacity adjustment factors of Table 310.15(B)(2)(a) must be applied. See 310.10 and 310.15 for details and examples.
NEC 310.15 - Ampacity
Also here is this:
310.4 Conductors in Parallel
By Mike Holt
Ungrounded and grounded neutral conductors sized 1/0 AWG and larger can be connected in parallel (i.e., electrically joined at both ends).
When conductors are run in parallel, the current must be evenly distributed between the individual parallel conductors. This is accomplished by ensuring that all ungrounded and grounded neutral conductors within a parallel set are identical. Each conductor of a parallel set must:
Be the same length.
Be made of the same conductor material (copper/aluminum).
Be the same size in circular mil area (minimum 1/0 AWG).
Use the same insulation material (like THHN).
Terminate in the same method (set screw versus compression).
In addition, raceways or cables containing parallel conductors must have the same physical characteristics and the same number of conductors in each raceway or cable. Conductors for one phase (ungrounded conductor) or the grounded neutral conductor, aren't required to have the same physical characteristics as those of another phase or grounded neutral conductor to achieve balance.
The equipment grounding (bonding) conductors for circuits in parallel must be identical to each other in length, material, size, insulation, and termination. In addition, each raceway (where required) must have an equipment grounding (bonding) conductor sized in accordance with 250.122. The minimum 1/0 AWG rule of 310.4 doesn't apply to equipment grounding (bonding) conductors [250.122(F)(1)].
When more than three current-carrying conductors are run together in a raceway longer than 24 inches, the ampacity adjustment factors of Table 310.15(B)(2)(a) must be applied. See 310.10 and 310.15 for details and examples.