1 reply to this topic

#1 knelli

knelli

    Project Manager

  • Senior Member
  • 157 posts
  • Interests:Horses, Winter sports, Wine and traveling
  • Discipline:Structural

Posted 27 January 2010 - 09:13 PM

Hi all,

I'll admit, I'm a newbie at Seismic Design for categories greater than B..... So, let me see if I have this right....

When is it required to apply the overstrength factor?
The overstrength factor should be used when certain vertical or horizontal irregularities apply and is dependent on SDC. ASCE 7-05 12.3.3.3 and 12.3.3.4 outline when overstrength should be used.

Am I missing anything?

Thanks! -K

#2 kevo_55

kevo_55

    The Beer Baron

  • Charter Member
  • 5,443 posts
  • Gender:Male
  • Location:MSP
  • Discipline:Structural

Posted 28 January 2010 - 12:38 AM

knelli,

You will use your overstrength factors when you have some sort of irregularity or when called for in the material's seismic provisions. You would also need to use the overstrength factor when designing drag struts with non light framed shear wall systems.

I hope this helps!