P pemaster New member Joined Aug 15, 2010 Messages 2 Reaction score 0 Sep 30, 2010 #1 What is the NEC code for conduit % fill for above ground conduit. this is with regards to the size. This is between the pole mount cabinet enclosure and the power pole. Thank you!
What is the NEC code for conduit % fill for above ground conduit. this is with regards to the size. This is between the pole mount cabinet enclosure and the power pole. Thank you!
Flyer_PE Jr. PE / Sr. Company Pilot Joined May 18, 2007 Messages 4,532 Reaction score 595 Location Tennessee Sep 30, 2010 #2 Article 344.22 directs you to Table 1 of Chapter 9. Table 1 of Chapter 9: 1 Conductor - 53% 2 Conductors - 31% >2 Conductors - 40%
Article 344.22 directs you to Table 1 of Chapter 9. Table 1 of Chapter 9: 1 Conductor - 53% 2 Conductors - 31% >2 Conductors - 40%