Wow, a new topic in the lonely electrical section. Why should the CE's have all the fun?
Okay, so I'm a transmission line guy and all I know about practical application of the NEC is what I learned in the two weeks I devoted to studying it prior to the PE, so I might need a little help here.
Our neighborhood pool pump motor smoked when they first fired it up for the season and the HOA pool lady emailed in a panic that it had to be replaced by next week. The electrical contractor says "the aluminum wiring caused the motor to overload and the lug connections to burn up". :th_rockon: With my skeptical toe itching like crazy, the contractor also wants to install a starter contacter and copper wiring for the three feet over to the motor to the tune of $3300. So I figured I'd better go check it out.
The motor is a 7.5HP, 230V, 1-phase, with SF=1.15, code F. It is protected by a 60A breaker. The wire to it is jacketed triplex aluminum, not sure what size that is and can't read the side since it's in conduit, but it looks plenty beefy to me (like triplex used to serve residence).
So I've never heard of "aluminum wiring" being the source of a failure (as opposed to unsufficiently sized wire, which makes no difference what the material is). I gave back my borrowed NEC book so can somebody tell me what the proper wire size and thermal overload protection is given the specs?
I suspect the motor may be rotor locked or otherwise fried, and installing a starter might be a nice addition, but the "aluminum wiring and lugs" story sounds fishy to my non-residential-expert ears.
Okay, so I'm a transmission line guy and all I know about practical application of the NEC is what I learned in the two weeks I devoted to studying it prior to the PE, so I might need a little help here.
Our neighborhood pool pump motor smoked when they first fired it up for the season and the HOA pool lady emailed in a panic that it had to be replaced by next week. The electrical contractor says "the aluminum wiring caused the motor to overload and the lug connections to burn up". :th_rockon: With my skeptical toe itching like crazy, the contractor also wants to install a starter contacter and copper wiring for the three feet over to the motor to the tune of $3300. So I figured I'd better go check it out.
The motor is a 7.5HP, 230V, 1-phase, with SF=1.15, code F. It is protected by a 60A breaker. The wire to it is jacketed triplex aluminum, not sure what size that is and can't read the side since it's in conduit, but it looks plenty beefy to me (like triplex used to serve residence).
So I've never heard of "aluminum wiring" being the source of a failure (as opposed to unsufficiently sized wire, which makes no difference what the material is). I gave back my borrowed NEC book so can somebody tell me what the proper wire size and thermal overload protection is given the specs?
I suspect the motor may be rotor locked or otherwise fried, and installing a starter might be a nice addition, but the "aluminum wiring and lugs" story sounds fishy to my non-residential-expert ears.