Voltage Drop Example Problem

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Evol

New member
Joined
Jul 26, 2021
Messages
2
Reaction score
0
This problems asks to find the voltage across the motor. Seems simple to just calculate the Voltage Drop across the conductors using Table 9. However since the current is given with an angle of -13 degrees isnt the power factor known? The answer key simply uses the effective Z given by a power factor of 0.85. Some help would be great thanks.

1627355787860.png

1627355801217.png
 
Cable resistance is directly from Table 9 under alternating Current Resistance for uncoated wires. Not sure where you see effective Z in the answer?

cos(13) = .97 so you are not using effective Z.

I get the same answer using the table and accounting for a 4000 foot run.
 