525.) Two single-phase transformers with identical voltage ratings are proposed to be connected in parallel to serve a load. The following rating and impedance data are provided:
Transformer 1: 1,000kVA, Z= 4.5%
Transformer 2: 2,000kVA, Z= 6.0%
The maximum total load (kVA) that can be served by the bank without overloading either transformer is most nearly:
A.) 2,333
B.) 2,500
C.) 2,667
D.) 3,000
Okay, I don't know much about paralleling transformers. Could someone give me an explanation on this one.....particularly on the solution's statement: "The transformers will load in inverse proportion to their impedances."
Thanks guys