NCEES Power Afternoon Problems 525 & 531, Need some clarification

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

chicago

Well-known member
Joined
Jun 23, 2007
Messages
48
Reaction score
0
Problem # 525) In the solution, the first phrase states "The transformers will load in inverse proportion to their impedances."

Problem # 531) In the solution, the first phrase states "The vars vary as the square of the applied voltage."

For both problems, I am not looking for help in deriving the solution they have posted, but rather an understanding of what they mean by the respective statements.

Appreciate your efforts in advance.

 
Problem 525: The parameter that determines how much load is carried by each transformer is the ratio of transformer impedances rather than the power rating of the transormers. It becomes essentially a current division problem. The lower impedance transformer will carry a greater portion of the total load.

Problem 531: The capacitor has a kvar rating at 240 volts. The application is on a 208 volt system. Power = V2/Z. Since Z in this case is fixed, the power will vary by the square of the voltage.

Let me know if this helps.

Jim

 
Jim, thanks for the feedback. I understand the problems better now.

For Problem 525, if I understand correctly, I could setup the equation as follows:

I2/I1 = Z1/Z2

correct?

 
The ratios are correct. The only thing to remember is that, since the impedances are given in percentages, they have to be converted to a common base. It doesn't matter if you convert Transformer 2 impedance to the Transformer 1 base or the other way around.

You can definitely expect to find a few problems that involve converting pu values from one base to another on the test.

Jim

 
i had the exact same question. thanks for clearing it up. i guess a lot of problems go back to that relationship, z=v^2/s! :)

 
525)

let's assume the PU V is 1

it will be the same for any xfmr in parallel

let's assume the following PU Z for each xfmr

T1 1

T2 1/2

T3 1/3

Tx 1/x

P=V^2/Z and V^2 = 1

P1 = 1/1 = 1

P2 = 1/(1/2) = 2 or 2 times (inverse of Z) P1

P3 = 1/(1/3) = 3....

Px = 1/(1/x) = x or x times (inverse of Z) P1

in other words they load inverse to their Z

531)

for any power (real P watts, complex S va, reactive Q var) the magnitude is proportional to V^2/Z

power is ALWAYS proportional to the square of the voltage (and the current I^2 Z)

 
Last edited by a moderator:
525)let's assume the PU V is 1

it will be the same for any xfmr in parallel

let's assume the following PU Z for each xfmr

T1 1

T2 1/2

T3 1/3

Tx 1/x

P=V^2/Z and V^2 = 1

P1 = 1/1 = 1

P2 = 1/(1/2) = 2 or 2 times (inverse of Z) P1

P3 = 1/(1/3) = 3....

Px = 1/(1/x) = x or x times (inverse of Z) P1

in other words they load inverse to their Z

531)

for any power (real P watts, complex S va, reactive Q var) the magnitude is proportional to V^2/Z

power is ALWAYS proportional to the square of the voltage (and the current I^2 Z)
Very good example representation Art. Put that in your notebooks guys.

John

 
Very good example representation Art. Put that in your notebooks guys.
John
thank you sir

I was taught well by good teachers...

do NOT memorize anything...

learn to derive the basics from the physics

and convince yourself of the rest mathematically...

know the basics and build on them...it's not a coincidence these tests are open book...

the FE a bit less though, because it tests the basics...

 
Back
Top