A synchronous generator is 3 phase wye connected and rated 1131 kva, 2.4 kv, 0.9 lagging. the output current from the generator at rated full load is most nearly:

Why do you use the formula Sbase = Sq root 3 Vbase Ibase

I just used the S=VI formula and got it wrong. Tad confused

 

Flyer_PE

Jr. PE / Sr. Company Pilot
EB Supporter
Joined
May 18, 2007
Messages
6,226
Reaction score
880
Location
Madiganistan
S=VI* is valid for single-phase devices.

S=sqrt3VI* is the power equation for three-phase devices.

 

roadrunner

Member
Joined
Jan 25, 2010
Messages
11
Reaction score
0
Thanks Flyer! Hope you know how important to this forum you are, your help is GREATLY appreciated

 

akyip

Member
Joined
Feb 7, 2020
Messages
377
Reaction score
135
Why is this not S=3*Vp*Ip... instead we used S=3*VL*IL
Typically, 3-phase voltage values are given as line-to-line voltages and 3-phase current values are given as line currents. If you are given 3-phase voltage/current/power values and they don't specify whether it's line-to-line or line-to-neutral values, you need to assume that:
  • the voltages given are line-to-line voltage values
  • the currents given are line current values
  • the power values given (W, VA, or VAR) are 3-phase power values
So here in this problem with the 3-phase synchronous generator, the 1131 KVA given is 3-phase apparent power and the 2.4 KV voltage given is line-to-line voltage. So |S 3-ph| = sqrt(3) x |V LL| x |I L|, and line current magnitude value |I L| = |S 3-ph| / (sqrt(3) x |V LL|).

I also attached a brief derivation of the apparent 3-phase power formula. Please note that this is magnitude only |S 3-ph|.
 

Attachments

  • S 3-ph derivation.jpg
    S 3-ph derivation.jpg
    38 KB · Views: 7

Zach Stone P.E.

Learn how to Pass the Power PE Exam at electricalp
EB Sponsor
Joined
Oct 25, 2016
Messages
377
Reaction score
175
Location
USA
A synchronous generator is 3 phase wye connected and rated 1131 kva, 2.4 kv, 0.9 lagging. the output current from the generator at rated full load is most nearly:

Why do you use the formula Sbase = Sq root 3 Vbase Ibase

I just used the S=VI formula and got it wrong. Tad confused

These are two different formulas. The first calculates the apparent power for a three-phase system or machine, and the second calculates the apparent power for a single-phase system or machine, or the per-phase power of a three-phase system or machine.

These two formulas are very commonly misused. If you'd like to dig further with more examples of how these can be used both correctly AND incorrectly, take a look at the following article: