NEC Code questions

Recommended Posts

This is a thread to ask NEC code related questions. 

Example16: What is the ampacityto size the feeder conductor if it supplies the following two motors?
1.One 7.5-hp, 230V, single-phase motor
2.One 5-hp, 230V, single-phase motor
Ans: Table 430.248 gives 40 A and 28 A as individual FLC of the two motors. Per Article 430.24, the feeder must be sized to 40x125%+28 = 78 A.
Size the conductor for 75 C terminals: Ans. 4 AWG (85A)

I would think the feeder conductor should be sized for 60C since it is less than 100 amps and motor design codes are not given. Can someone verify? 

 

Share this post


Link to post
Share on other sites

image.png.92c3b9ebc2650fa4efc2e01894517cf6.png

XHHW can be found in 75C and 90 C insulation.  This problem may have been solved using previous years code. According to 2017 code, does wet location mean 75C insulation? I have not been able to find that.  

Share this post


Link to post
Share on other sites
On 3/3/2019 at 9:33 AM, roy167 said:

image.png.92c3b9ebc2650fa4efc2e01894517cf6.png

XHHW can be found in 75C and 90 C insulation.  This problem may have been solved using previous years code. According to 2017 code, does wet location mean 75C insulation? I have not been able to find that.  

I think i remember reading somewhere that most of the terminal equipment is rated at 75C, so 75 C is chosen as its more common? I'm not completly sure on that, just wanted to provide some input

Share this post


Link to post
Share on other sites
On 3/3/2019 at 11:01 AM, roy167 said:

This is a thread to ask NEC code related questions. 

Example16: What is the ampacityto size the feeder conductor if it supplies the following two motors?
1.One 7.5-hp, 230V, single-phase motor
2.One 5-hp, 230V, single-phase motor
Ans: Table 430.248 gives 40 A and 28 A as individual FLC of the two motors. Per Article 430.24, the feeder must be sized to 40x125%+28 = 78 A.
Size the conductor for 75 C terminals: Ans. 4 AWG (85A)

I would think the feeder conductor should be sized for 60C since it is less than 100 amps and motor design codes are not given. Can someone verify? 

 

 

On 3/3/2019 at 11:33 PM, roy167 said:

image.png.92c3b9ebc2650fa4efc2e01894517cf6.png

XHHW can be found in 75C and 90 C insulation.  This problem may have been solved using previous years code. According to 2017 code, does wet location mean 75C insulation? I have not been able to find that.  

If no other adjustments or correction factors are given use 75degC. You can see in NEC'17_Annex D Example D7 doing the same .

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...

×
×
  • Create New...