A 1,000 KVA, 12.47KV- 480Y/277-V transformer with 4% impedance feeds a 480-V bus. The fault duty of the 12.47-KV system is 40MVA. Assuming the transformer and the 12.47KV system have the same X/R ratio, the 3-phase short circuit current(Amperes) avaliable at the 480-V bus is mostlynearly:

I am having difficulties visualizing this problem. Can you anyone tackle this problem on a step by step process?.

-What so they mean by same "X/R ratio"?

Thanks!!

 
Look up the MVA Method for solving this problem.

 
Last edited by a moderator:
A 1,000 KVA, 12.47KV- 480Y/277-V transformer with 4% impedance feeds a 480-V bus. The fault duty of the 12.47-KV system is 40MVA. Assuming the transformer and the 12.47KV system have the same X/R ratio, the 3-phase short circuit current(Amperes) avaliable at the 480-V bus is mostlynearly:

I am having difficulties visualizing this problem. Can you anyone tackle this problem on a step by step process?.

-What so they mean by same "X/R ratio"?

Thanks!!
This is a Per Unit problem for me.

1. Choose a system 3-phase power base to be 1000 KVA (I chose the transformer base just for simplicty)

2. Your I_fault in per unit will be V/Z_total

V in per unit is 1 at an angle of zero degrees for our voltage source

Z_total = Z_transformer per unit + Z_transmission line per unit

Z_transformer per unit is given on a 1 MVA base which matches our chosen MVA base so we don't have to convert it, Z_transformer = j0.04

Z_transmission per unit is equal to MVA_Base_3_Phase/Fault_Duty_3_Phase = 1 MVA/40MVA = j0.025 (I remember this formula from grad school)

Z_total = j0.025 + j0.04 = j0.065 per unit (transformer in series with transmission line)

I_Fault = ( per unit voltage)/(0.065) = 15.38 per unit

Now we need to find our I_Base at the 480V bus to obtain I_actual:

I_Base_480V = (S_Base_Single_Phase)/(V_Base_Phase) = (333,333 VA/277 V) = 1203.37 A

I_Actual = I_Fault_Per_Unit * I_Base_480V = 15.38 * 1203.37 A = 18,507.82 A

Not sure if this matches how they solved it exactly, but that's how I would solve it.

Hope this helps.

 
Last edited by a moderator:
A 1,000 KVA, 12.47KV- 480Y/277-V transformer with 4% impedance feeds a 480-V bus. The fault duty of the 12.47-KV system is 40MVA. Assuming the transformer and the 12.47KV system have the same X/R ratio, the 3-phase short circuit current(Amperes) avaliable at the 480-V bus is mostlynearly:

I am having difficulties visualizing this problem. Can you anyone tackle this problem on a step by step process?.

-What so they mean by same "X/R ratio"?

Thanks!!
Go thru this for "X/R ratio"

http://www.brainfiller.com/documents/XRRatio.pdf

 
Very Neat!!!!!

I didn't know about the following formula: ":Transmission per unit is equal to MVA_Base_3_Phase/Fault_Duty_3_Phase " but your approach makes perfectly sense to me. I would be curious to know how they derived this formula. Can you email, post or refer me to a book talking about Fault_Duty_3_Phase? Not much time left for April exam.

Thanks!!!!

 
A 1,000 KVA, 12.47KV- 480Y/277-V transformer with 4% impedance feeds a 480-V bus. The fault duty of the 12.47-KV system is 40MVA. Assuming the transformer and the 12.47KV system have the same X/R ratio, the 3-phase short circuit current(Amperes) avaliable at the 480-V bus is mostlynearly:

I am having difficulties visualizing this problem. Can you anyone tackle this problem on a step by step process?.

-What so they mean by same "X/R ratio"?

Thanks!!
This is a Per Unit problem for me.

1. Choose a system 3-phase power base to be 1000 KVA (I chose the transformer base just for simplicty)

2. Your I_fault in per unit will be V/Z_total

V in per unit is 1 at an angle of zero degrees for our voltage source

Z_total = Z_transformer per unit + Z_transmission line per unit

Z_transformer per unit is given on a 1 MVA base which matches our chosen MVA base so we don't have to convert it, Z_transformer = j0.04

Z_transmission per unit is equal to MVA_Base_3_Phase/Fault_Duty_3_Phase = 1 MVA/40MVA = j0.025 (I remember this formula from grad school)

Z_total = j0.025 + j0.04 = j0.065 per unit (transformer in series with transmission line)

I_Fault = ( per unit voltage)/(0.065) = 15.38 per unit

Now we need to find our I_Base at the 480V bus to obtain I_actual:

I_Base_480V = (S_Base_Single_Phase)/(V_Base_Phase) = (333,333 VA/277 V) = 1203.37 A

I_Actual = I_Fault_Per_Unit * I_Base_480V = 15.38 * 1203.37 A = 18,507.82 A

Not sure if this matches how they solved it exactly, but that's how I would solve it.

Hope this helps.
Thanks sam314159. Neat job!!!

 
A 1,000 KVA, 12.47KV- 480Y/277-V transformer with 4% impedance feeds a 480-V bus. The fault duty of the 12.47-KV system is 40MVA. Assuming the transformer and the 12.47KV system have the same X/R ratio, the 3-phase short circuit current(Amperes) avaliable at the 480-V bus is mostlynearly:

I am having difficulties visualizing this problem. Can you anyone tackle this problem on a step by step process?.

-What so they mean by same "X/R ratio"?

Thanks!!
Go thru this for "X/R ratio"

http://www.brainfiller.com/documents/XRRatio.pdf
I will double check the site. Thanks!!

 
A 1,000 KVA, 12.47KV- 480Y/277-V transformer with 4% impedance feeds a 480-V bus. The fault duty of the 12.47-KV system is 40MVA. Assuming the transformer and the 12.47KV system have the same X/R ratio, the 3-phase short circuit current(Amperes) avaliable at the 480-V bus is mostlynearly:

I am having difficulties visualizing this problem. Can you anyone tackle this problem on a step by step process?.

-What so they mean by same "X/R ratio"?

Thanks!!
MVA Method

40MVA in series with 25 MVA (1MVA/.04)

40 X 25 / (40+25) = 15.38 MVA

Fault is on the 480v bus

15.38MVA/(sqrt(3) * 480e-6MV) = 18,500A

 
A 1,000 KVA, 12.47KV- 480Y/277-V transformer with 4% impedance feeds a 480-V bus. The fault duty of the 12.47-KV system is 40MVA. Assuming the transformer and the 12.47KV system have the same X/R ratio, the 3-phase short circuit current(Amperes) avaliable at the 480-V bus is mostlynearly:

I am having difficulties visualizing this problem. Can you anyone tackle this problem on a step by step process?.

-What so they mean by same "X/R ratio"?

Thanks!!
MVA Method

40MVA in series with 25 MVA (1MVA/.04)

40 X 25 / (40+25) = 15.38 MVA

Fault is on the 480v bus

15.38MVA/(sqrt(3) * 480e-6MV) = 18,500A
The MVA method seems to be shorter but it feels good to know more than one method.

Thanks for your quick response. Great forum!!

 
http://www.arcadvisor.com/pdf/ShortCircuitABC.pdf

MVA method. VERY useful to learn. Doesn't take much to "master". It's very good for double-checking your work on the exam. IIRC, there were a couple problems on the exam, I worked them different ways (one way was MVA method) and got the same answer, so I was confident in my answer on those.

 
http://www.arcadvisor.com/pdf/ShortCircuitABC.pdf
MVA method. VERY useful to learn. Doesn't take much to "master". It's very good for double-checking your work on the exam. IIRC, there were a couple problems on the exam, I worked them different ways (one way was MVA method) and got the same answer, so I was confident in my answer on those.
Thanks a lot cableguy. Very useful!! I am getting very confident for the April exam. 2 more weeks to go.

 
http://www.arcadvisor.com/pdf/ShortCircuitABC.pdf
MVA method. VERY useful to learn. Doesn't take much to "master". It's very good for double-checking your work on the exam. IIRC, there were a couple problems on the exam, I worked them different ways (one way was MVA method) and got the same answer, so I was confident in my answer on those.
good material,,,,

i have a question in the phase - ground claculation shown on page 4.7.6 in the document u attached... i dont know how they have shown three branches (fig 18) .

shouldn't there be only two branches... where the third branch came from... any help thanks....

 
I searched for "branches" in this forum for the exact question you have, Ros. I do not understand this MVA method paper's calculation of SLG fault. Does anyone know why there are three branches?

 
I think I figured out Moon's MVA Method for SLG fault (single phase to ground fault). He has three branches, as if it is a 3PH fault. And then he calculates the current as if it were a 3 phase fault, meaning he uses the formula Isc_SLG = MVAsc / (rad(3) * V_LL). In this case, MVAsc = 3*MVAsc_SLG.

To me, it is more intuitive to just use one branch (all three branches are the same anyway, that's why he could simply multiply by 3). The key here is to remember to use the Line-to-neutral, or line-to-ground voltage. After all, this is a single-LINE-To-GROUD fault, right??

Isc_SLG = MVAsc_SLG / (V_LN) = MVAsc_SLG / ( V_LL / rad(3) )

You'll get the same answer either way. It's more intuitive to me to use one branch because that's what the sequence network looks like in my power book!

 
Sorry for bringing an old thread back to life, but what is the significance of the problem statement "Assuming the transformer and the 12.47KV system have the same X/R ratio...
"? What if this were not the case?

 
They're just telling you the angles for the impedances of the system and the transformer are the same. It makes the vector math a little easier. It usually isn't a factor though since one impedance will typically be several orders of magnitude away from the other making the delta in the angles irrelevant.

 
This problem can also be solved using the per-unit method.

  1. When using the per-unit method there is an impedance associated with the fault duty.
  2. This obtained first by getting the per-unit apparent power which is found by using the 1000kVA rating of the transformer the system's base apparent power and converting it into MVA, which is 1MVA. Next the fault duty's per-unit value is S=40MVA / 1MVA = 40p.u.
  3. Next the per-unit impedancnce associated with the fault duty is z =vpu2 / spu= 12 / 40 = .025pu.
  4. Next we find the per-unit fault current is
  5. i.fault_pu = 1 / (.04+.025) = 15.38pu.Next the base current on the secondary side of the transformer where the fault occurs is Ib = (1000*103) / (sqrt(3) * 480 ) = 1202.81Amps
  6. Finally we determine the acctual fault current by multiplying the per-unit fault current by the base current on the secondary side of the transformer.
IFAULT = i.fault_pu * Ib = (15.38)*(1202.81) = 18499 Amps.

 
Last edited by a moderator:
MVA Method

40MVA in series with 25 MVA (1MVA/.04)

40 X 25 / (40+25) = 15.38 MVA

Fault is on the 480v bus

15.38MVA/(sqrt(3) * 480e-6MV) = 18,500A
Thank you for this.  I started the PU method but it looked too lengthy.  The MVA method is much simpler and easier to solve with.

 