Do GFCI receptacles require dedicated neutral?
#1
Posted 14 June 2011 - 12:05 AM
Am I correct to think that if both receptacles are in use at the same time the first receptacle will trip since the current differential will be different, due to the shared neutral?
#2
Posted 14 June 2011 - 02:17 AM
#3
Posted 14 June 2011 - 04:22 PM
My question was about the neutral. And you answered it by saying "Each GFCI does require a dedicated hot and neutral".
#4
Posted 11 January 2012 - 08:55 PM
#5
Posted 11 January 2012 - 09:28 PM
If I understand this correctly (I'm not an electrical guy) if one installs a GFCI on given circuit, then any subsequent regular outlets further away from the panel and on the same circuit are also protected. correct?
QUOTE (wilheldp_PE @ Jun 13 2011, 07:17 PM)
Are you talking about a ground or a neutral. Each GFCI does require a dedicated hot and neutral, but you can daisy-chain the ground. The way you would normally install two GFCI protected outlets is to put the GFCI closest to the panel, then daisy-chain a regular outlet off of it. If you put another GFCI downstream of a GFCI, it will not work correctly.
My question was about the neutral. And you answered it by saying "Each GFCI does require a dedicated hot and neutral".
#6
Posted 11 January 2012 - 09:49 PM
Suppose we have two GFCI receptacles. The first is on Circuit 1 and the other is on Circuit 3. They are both fed from the same panel. They both share a neutral wire.
Am I correct to think that if both receptacles are in use at the same time the first receptacle will trip since the current differential will be different, due to the shared neutral?
You probably don't want to share the neutral between 2 circuits normally. Also, GFCI works by sensing the returning current on the Line and Neutral so it would most likely trip both devices due to a single fault.
#7
Posted 19 June 2012 - 12:47 PM
If I understand this correctly (I'm not an electrical guy) if one installs a GFCI on given circuit, then any subsequent regular outlets further away from the panel and on the same circuit are also protected. correct?
QUOTE (wilheldp_PE @ Jun 13 2011, 07:17 PM)
Are you talking about a ground or a neutral. Each GFCI does require a dedicated hot and neutral, but you can daisy-chain the ground. The way you would normally install two GFCI protected outlets is to put the GFCI closest to the panel, then daisy-chain a regular outlet off of it. If you put another GFCI downstream of a GFCI, it will not work correctly.
My question was about the neutral. And you answered it by saying "Each GFCI does require a dedicated hot and neutral".
That is correct as long as the receptacles downstream are wired to the LOAD side of the GFCI receptacle and not just daisy chained off of the LINE wiring into the receptacle.