I have some extra time today and decided to compare all the various voltage drop methods (there are a few)...both single & 3 phase problems.
Methods are Ugly's handbook, Bussmann chart, and of course the PE NCEES method using Chapter 9, Table 9. I wanted to see if there were differences...and the results were interesting.
Here's what I came up with:
Problem #1
Single Phase, 240 Volt, #8 THWN, 30 amperes, 150 feet
Ugly's 2008 handbook:
Vd = (2 x K [copper constant] x L (distance) x I ) / circular mills
= (2 x 12.9 x 50 x 3)/16,510
= 7.03 volts
Bussmann: 150 feet x 30 amperes = 4500
4500 x 1520 [100% pf, single phase for #8 wire] = 6,840,000
Divide by 10^6: 6.84 volts
PE method: Z = (.78 + j.065) * ((150 * 2)/1000)
= .234 + j.0195
I * Z = 30 (.234 + j.0195)
= 7.04 volts
So far so good...all 3 yielding similar results.
3 phase is next and this is where the fun begins.
Voltage Drop
Started by
audioaddict
, Jun 14 2010 03:55 PM
7 replies to this topic
#1
Posted 14 June 2010 - 03:55 PM
#2
Posted 14 June 2010 - 04:00 PM
Now I'm taking problem #129 from the Power NCEES problem set:
Three phase, 480 Volt, 500 kcmil, 400 amps, 250 feet, .8 lagging pf
Ugly's:
Vd = (1.73x 12.9 x 250 x 400)/500,000
= 4.47 volts
Bussmann:
250' x 400A = 100,000
100,000 x 85 [bussmann table, 500kcmil @ 80% pf, 3 ph] = 8,500,000
Divide by 10^6:
8.5 volts
PE method gives 9.72 volts....I can type it out if people want.
A bit of variance here....makes you think a little.
What's annoying is the company excel spreadsheet seems spot on with Ugly's...which comes out low. Ugh!
Maybe I made a mistake (doubt it since I checked it over a few times)....but something is up.
Any ideas?
Three phase, 480 Volt, 500 kcmil, 400 amps, 250 feet, .8 lagging pf
Ugly's:
Vd = (1.73x 12.9 x 250 x 400)/500,000
= 4.47 volts
Bussmann:
250' x 400A = 100,000
100,000 x 85 [bussmann table, 500kcmil @ 80% pf, 3 ph] = 8,500,000
Divide by 10^6:
8.5 volts
PE method gives 9.72 volts....I can type it out if people want.
A bit of variance here....makes you think a little.
What's annoying is the company excel spreadsheet seems spot on with Ugly's...which comes out low. Ugh!
Maybe I made a mistake (doubt it since I checked it over a few times)....but something is up.
Any ideas?
#3
Posted 14 June 2010 - 08:36 PM
QUOTE (audioaddict @ Jun 14 2010, 09:00 AM) <{POST_SNAPBACK}>
Any ideas?
The second line on the page: "Inductance Negligible"
#4
Posted 16 June 2010 - 03:20 PM
QUOTE (BryGuy @ Jun 14 2010, 04:36 PM) <{POST_SNAPBACK}>
QUOTE (audioaddict @ Jun 14 2010, 09:00 AM) <{POST_SNAPBACK}>
Any ideas?
The second line on the page: "Inductance Negligible"
Sorry, I don't understand.
#5
Posted 16 June 2010 - 06:23 PM
PE method, Ohms law, all the way, all the time. Ohms law is all that is required.
#6
Posted 21 June 2010 - 06:54 PM
QUOTE (pelaw @ Jun 16 2010, 02:23 PM) <{POST_SNAPBACK}>
PE method, Ohms law, all the way, all the time. Ohms law is all that is required.
Makes me appreciate my degree that much more.
BTW, power factor seems to be irrelevant to the actual value of voltage drop (who cares about angle?) but the Bussman tables seem to think they matter.
Interesting that they could make such a mistake.
Edited by audioaddict, 21 June 2010 - 06:55 PM.
#7
Posted 21 June 2010 - 07:13 PM
^The thing to remember for things like the Bussman tables is that they are providing direction to select a protective device. The numbers they generate for the tables will be generated ignoring details that, while affecting the actual numeric answer, will not affect which device you select.
#8
Posted 27 June 2010 - 05:08 AM
In smaller gage cables and shorter runs resistance is what will cause voltage drop so the higher the power factor the more voltage drop you can expect. Take for instance the IEEE Red Book's approximate formula V=IRcos(angle) + IXsin(angle) the higher the angle the smaller the pf the less percentage of IR contribution and the more percentage of IX, but since X is low for small gage short runs the voltage drop will be small. At 500kcmil the reactance is higher than the resistance so smaller pf's will have a higher voltage drop. It's not until 300kcmil where the reactance starts passing the resistance.
The Ugly's book is intended for residential and small commercial building applications where resistance dominates and power factors are typically high. Certain references in the Ugly's book is intended for on the fly calculations which is not acceptable for Engineering applications.
The Ugly's book is intended for residential and small commercial building applications where resistance dominates and power factors are typically high. Certain references in the Ugly's book is intended for on the fly calculations which is not acceptable for Engineering applications.