NCEES 2008 problem #501

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

PEin2010

Well-known member
Joined
Aug 29, 2010
Messages
86
Reaction score
0
Location
California
Why is the answer 63 kips (ASD) / 94 (LRFD) and not 125 kips (ASD) / 187 (LRFD)???

When to use the maximum uniform load given by the table and when to use the Vn/ factor of safety (the value given at the bottom of the column on pg. 3-74 / AISC manual)???

Thank you!

 
Why is the answer 63 kips (ASD) / 94 (LRFD) and not 125 kips (ASD) / 187 (LRFD)???
When to use the maximum uniform load given by the table and when to use the Vn/ factor of safety (the value given at the bottom of the column on pg. 3-74 / AISC manual)???

Thank you!

Don't have the question in front of me, but I'm pretty sure that shear failure governs in that case. Max shear is 94 kips

 
If the load were fixed at the center, then you would multiply the allowable shear load by 2. But this is a MOVING load, so if the load were placed nearest to one of the ends, then shear governs (62.5 k) as the allowable shear force would equal the applied load.

 