Spin-Up is now providing the "PE Power Question for the Week" http://www.spinupexams.com/

The Question For The Week will help those taking the Power PE exam.

The way it works is:

1. Every Monday a new question is provided on the "Question For The Week" tab on http://www.spinupexams.com/ no multiple choices will be provided on Monday's. Attempt to solve the problem without any multiple choices available.

2. On Wednesday's the multiple choices will be provided.

3. On Friday's the complete solution will be provided

4. This will be repeated every week with a new sample exam question.

Enjoy the Question For The Week. Let us know of any improvements you would like to see for the "Question For The Week"

Good Luck on your studies!

Joan

 
I'm taking PE Electrical Power. Could you suggest me the book. I bought NCEES book (Electrical & Computer : Power - 64 pages), and I don't have any extensive books for the preparation. Which book is the best?

 
Spin-Up is now providing the "PE Power Question for the Week" http://www.spinupexams.com/

The Question For The Week will help those taking the Power PE exam.

The way it works is:

1. Every Monday a new question is provided on the "Question For The Week" tab on http://www.spinupexams.com/ no multiple choices will be provided on Monday's. Attempt to solve the problem without any multiple choices available.

2. On Wednesday's the multiple choices will be provided.

3. On Friday's the complete solution will be provided

4. This will be repeated every week with a new sample exam question.

Enjoy the Question For The Week. Let us know of any improvements you would like to see for the "Question For The Week"

Good Luck on your studies!

Joan
I like the question for the week, but can the solution be posted at the same time as the question. It makes it more convenient that way. I prefer not to have to wait until Friday.

 
I agree! Post them at the same time.

Can you keep the prior week's question up also, incase I forget to look one week.

 
Thank You for the feedback.

The solution has been uploaded for the QFTW. Both Question and Solution will be uploaded at the same time.

The question and solution from the prior week will be made available.

Let me know what other changes you would like.

http://www.spinupexams.com/

Joan

 
Last edited by a moderator:
Thank You for the feedback.

The solution has been uploaded for the QFTW. Both Question and Solution will be uploaded at the same time.

The question and solution from the prior week will be made available.

Let me know what other changes you would like.

http://www.spinupexams.com/

Joan

Spin-up, regarding the answer for that question....since the 480V Line to line was given as 0 degrees....V phase lags or leads the line voltage by 30 degrees depending on the sequence....so the voltage could be 277<-30 or 277<+30....i don't have my references with me...but i'm sure the 30 degrees needs to be added to the equation, that's something that needs to be checked. A problem that NCEES added the 30 degree difference is in one of the NCEES practice problems I don't remember the problem #. I took all my references to my dads home and leave it there for good i didn't want to touch a book in a loonggg timee. But if some one have their references please clarify. I don't remember if it was the voltage or the current that the 30 degrees needs to be added.

 
Thank You for the feedback.

The solution has been uploaded for the QFTW. Both Question and Solution will be uploaded at the same time.

The question and solution from the prior week will be made available.

Let me know what other changes you would like.

http://www.spinupexams.com/

Joan

Spin-up, regarding the answer for that question....since the 480V Line to line was given as 0 degrees....V phase lags or leads the line voltage by 30 degrees depending on the sequence....so the voltage could be 277<-30 or 277<+30....i don't have my references with me...but i'm sure the 30 degrees needs to be added to the equation, that's something that needs to be checked. A problem that NCEES added the 30 degree difference is in one of the NCEES practice problems I don't remember the problem #. I took all my references to my dads home and leave it there for good i didn't want to touch a book in a loonggg timee. But if some one have their references please clarify. I don't remember if it was the voltage or the current that the 30 degrees needs to be added.
There is either a +/- 30 deg added when converting from Line-Line to Line-Neutral. if I remember correctly in a balanced a-b-c sequence there is a -30 deg going from line-line to line-neutral. For a a-c-b sequence we add +30 deg going from line-line to line-neutral. In Spin-Up's problem the angle is not given for the voltage nor indicated if it is a positive or negative sequence. But that is not needed since PF is relative between the voltage angle and current angle. Since the problem states the load has a 0.75 lagging PF we know that the angle is 41.4 deg. Since current lags voltage, we get the minus sign. Looking at spin-ups solution, it does not show the angle for voltage, but I do not think it is needed since we already know the angle between current and voltage. If we knew the current instead, but not the power factor, then knowing the voltage angle is critical because we need it to find the delta between the two angles to solve for pf. In my opinion, the answer spin-up has is correct. What does others think.

It is amazing that I know this stuff better now two months after finishing studying. Not sure if I needed time for the info to sink in or I have more confidence now after knowing that I passed the exam.

In the NCEES problem, i remember that we needed to use the angle because we converted from a delta configuration to like a virtual neutal to simplify the problem and then converting back. i think it was problem NCEES 111.

 
Last edited by a moderator:
Thank You for the feedback.

The solution has been uploaded for the QFTW. Both Question and Solution will be uploaded at the same time.

The question and solution from the prior week will be made available.

Let me know what other changes you would like.

http://www.spinupexams.com/

Joan

Spin-up, regarding the answer for that question....since the 480V Line to line was given as 0 degrees....V phase lags or leads the line voltage by 30 degrees depending on the sequence....so the voltage could be 277<-30 or 277<+30....i don't have my references with me...but i'm sure the 30 degrees needs to be added to the equation, that's something that needs to be checked. A problem that NCEES added the 30 degree difference is in one of the NCEES practice problems I don't remember the problem #. I took all my references to my dads home and leave it there for good i didn't want to touch a book in a loonggg timee. But if some one have their references please clarify. I don't remember if it was the voltage or the current that the 30 degrees needs to be added.
There is either a +/- 30 deg added when converting from Line-Line to Line-Neutral. if I remember correctly in a balanced a-b-c sequence there is a -30 deg going from line-line to line-neutral. For a a-c-b sequence we add +30 deg going from line-line to line-neutral. In Spin-Up's problem the angle is not given for the voltage nor indicated if it is a positive or negative sequence. But that is not needed since PF is relative between the voltage angle and current angle. Since the problem states the load has a 0.75 lagging PF we know that the angle is 41.4 deg. Since current lags voltage, we get the minus sign. Looking at spin-ups solution, it does not show the angle for voltage, but I do not think it is needed since we already know the angle between current and voltage. If we knew the current instead, but not the power factor, then knowing the voltage angle is critical because we need it to find the delta between the two angles to solve for pf. In my opinion, the answer spin-up has is correct. What does others think.

It is amazing that I know this stuff better now two months after finishing studying. Not sure if I needed time for the info to sink in or I have more confidence now after knowing that I passed the exam.

In the NCEES problem, i remember that we needed to use the angle because we converted from a delta configuration to like a virtual neutal to simplify the problem and then converting back. i think it was problem NCEES 111.
I disagree (with EEVA I think) , the answer provided is correct ONLY IF we assume Van angle is 0. It would also be a reasonable assumption to assume that VAB is at an angle of 0 and then the solution given is incorrect. If you are giving a solution with an angle it has to be respect to something. A simple addition of "Assume positive phase sequence and angle of Van = 0 would straighten it up.

 
Last edited by a moderator:
I believe DK PE is on the right track. Line-line voltages lag line-neutral voltages by 30 degrees, this is true. But we're not interested in that here. We're determining phase A current angle with respect to phase A voltage angle. Power factor is really given on a per phase basis (as it relates to impedance, which is a per phase quantity). The inverse cosine of the power factor will give you the angle between current and voltage. It doesn't matter what that voltage angle reference is. The current lags that reference by 41.4 degrees.

 
I believe DK PE is on the right track. Line-line voltages lag line-neutral voltages by 30 degrees, this is true.
Think you need to be more specific... the line to line VAB LEADS Van by 30 degrees, not lags, correct? I assume positive phase sequence.

The current lags that reference by 41.4 degrees.
You are correct, the problem would be correct if written "what is the current?" and added "(assume the voltage across the load is the reference at 0°)".

 
Ah yes, my mistake. LL voltages leads LN voltage by 30 degrees.

As to whether the question is written wrong... well, that's hard to say. It doesn't specifically say that Va is at 0 degrees, but I've always understood that to be a common assumption.

 
Clarity information has been provided to the QFTW. http://www.spinupexams.com/

A little vagueness is sometimes a good thing, it stirs up discussion and creates a learning environment. Sometimes vagueness is not good.

We appreciate the feedback.

Joan

 
Last edited by a moderator:
About this week NEC - Design B motor question:(determination motor HP)

Starting current is equal to locked rotor current only for DOL (direct on-line) stating method. In other case, in starting lower voltage is applied, so starting current is lower than locked rotor current.

Thanks,

 
About this week NEC - Design B motor question:(determination motor HP)

Starting current is equal to locked rotor current only for DOL (direct on-line) stating method. In other case, in starting lower voltage is applied, so starting current is lower than locked rotor current.

Thanks,
Insaf, Thanks for your feedback. I will forward your comment on.

Joan

 
This week's Question For The Week (QFTW) has been uploaded. Previous week's QFTW has been placed in the Previous Questions menu tab.

/>http://www.spinupexams.com/

Joan

 
Should the answer to the QFTW be found using Z-WYE = Z-DELTA / 3 for each leg?

 
Should the answer to the QFTW be found using Z-WYE = Z-DELTA / 3 for each leg?
Maybe take another peek at delta/wye transformation relationship when the leg impedances are not equal...

 